Electronic – Calculate minimum voltage to turn off/on solid state relay

relaysolid-state-relay

I have an AQZ204 AC/DC type solid state relay AQZA204 datasheet

Basically I want to calculate the minimum supply voltage required to turn the relay on

and the minimum supply voltage required to turn the relay off. These are similar to Pick/Drop voltages of mechanical relays or must be on voltage, must be off voltage..

I'm using 31.5 volt DC supply, with a series 4.7k Ohm Resistor to the input LED of the relay.

The data sheet is a little confusing to me, it saids the LED max dropout voltage is 1.5V so I calculated around 6.38mA forward current for the LED:

31.5VDC - 1.5Leddrop = 30VDC/4700 = 6.38mA

I'm confused by the IFon current being 3mA max?

So I can test the relays to see if they are in spec.

Best Answer

The IfOn Max current is the current that the least sensitive relay should require to turn in - most will turn on at lower currents, but you should supply at least 3 mA to ensure that any relay will be on. The Ablosute Maximum LED current is 50 mA, so it is safe to supply more than 3 mA.

For turn-off, there is IfOff Minimum of 0.4 mA - most units will turn off at a higher current, but the most sensitive may stay on with currents as low as 0.4 mA, so you should ensure that the LED current is below 0.4 mA when you want the thing to be off.