I've been trying to figure out how to estimate the settling time of a second order system in response to a step input of magnitude 5.
The systems transfer function is $$G(s) = \frac{1}{(s+2)(s+4)}$$ and I have already determined the time response with the step input R(s): $$C(s)=R(s)G(s)\qquad \therefore c(t) = \frac{5}{8}+\frac{5}{8}e^{-4t}-\frac{5}{4}e^{-2t}$$
Now I need to estimate the 2% settling time of the response using this information, but I'm not sure how. I know the system is overdamped as ΞΆ>1, so I can't use the normal settling time equation $$T_s =\frac{4}{\zeta\omega_n}$$
I looked into this post: (over and critically damped systems settling time) but the answers only explain long winded ways to get an accurate result. I've already used MATLAB to obtain an exact result of 2.3 seconds, but I need to be able to estimate it without MATLAB.

I was thinking I could try trial and error with different values of t until c(t) is within 2% of the steady state value (which is 0.625) but while this would work I doubt its the correct way to do it, so is anyone able to help me out with a better method?

Best Answer

For systems with real left-half plane poles, you can usually estimate it by only considering the dominant pole (the pole with the lowest frequency). In your case this would be \$p_d=-2\$. The result gets more accurate as the non-dominant pole (\$p_{nd}\$) moves further away from the dominant pole.

By only considering the dominant pole, you get a rather simple equation:

$$\begin{align} \frac{5}{4}\cdot e^{-2t}&=0.02\cdot \frac{5}{8} \\ t &= -\frac{1}{2}\cdot \ln\left( 0.02\cdot \frac{5}{8}\cdot \frac{4}{5} \right) \approx 2.30258509299s\\ \end{align}$$

The idea is that the non-dominant pole at \$p_{nd}=-4\$ leads to a term \$e^{-4t}\$ which will be damping so quickly that it doesn't affect the overall settling time. The advantage is the simplicity of the equation, and the fact that is actually a pretty common occurrence to have a very dominant pole and far-away non-dominant poles in electronic circuits.

In your specific case, it is possible to analytically calculate the settling time. The time it takes for the time-dependent terms to damp to 2% of the final value can be calculated using (similar to Andy's answer, but using the absolute value):

$$\begin{align} \left| e^{-4t}-2\cdot e^{-2t} \right| &=0.02 \\ &\Updownarrow (y=e^{-2t})\\ y^2-2\cdot y &= \pm 0.02 \\ &\Updownarrow (\text{There are 4 distinct solutions, but I only take the relevant one}) \\ y = e^{-2t} &= 1 - \frac{7}{5\sqrt{2}} \\ &\Updownarrow \\ t &= -\frac{1}{2}\cdot \ln\left(1 - \frac{7}{5\sqrt{2}}\right) \approx 2.30006613189s \end{align}$$

So a factor of 2 for \$p_{nd}/p_d\$ leads to about an error of 0.1% on the calculated settling time when using the dominant-pole approximation. Whether or not this is sufficient I leave to you.