Electronic – Measure voltage difference between ground and DC floating power supply lines

groundmultimeterpower supplyswitch-mode-power-supply

110/220V AC to 12V DC switching mode power supply
(metal enclosed, input is 220V with separate L,N and ground.)

  • Measured voltage difference with a multimeter between V- and V+ 12V
    DC as expected
  • Measured voltage difference between ground and V- or ground and V+
    reads practically 0V DC

According to this text about floating power supplies:

For floating DC power supplies, the voltage potential appears from
the positive output terminal to the negative output terminal. There is
no voltage potential (at least, none with any power behind it) from
either the positive terminal to earth ground or from the negative
output terminal to earth ground.

So that is in accordance with my measurement, but how can this be?
If there is a voltage different between point A and B in any electrical network, how can the voltage C-A and C-B both be zero?
The only explanation I can think of is a measuring error (multimeter ties the measured line to the ground?), but if so, the quoted text above is wrong?

Best Answer

Because the supply is floating, and you only made one measurement at once.

Floating means isolated, which means the resistance between the supply and ground is very very high. So high that the 10 Mohm input resistance of your multimeter is almost a short circuit in comparison.

schematic

simulate this circuit – Schematic created using CircuitLab

If you were to make both measurements at once, with identical meters, you would find V- at -6V and V+ at +6V with respect to ground, and 12V of course between V- and V+.