Electronic – Why do you need a thicker wire when wire length increases

dcgaugeresistancewire

Question:

So far I've found that the thickness of the wire influences the resistance. A thicker wire has less resistance. Also, the length of a wire has a linear correlation with the resistance. 2x length = 2x resistance. So your wire resistance will be length / thickness, but that doesn't explain why the thickness should increase with length. What am I missing?

Elaboration:

I can think of two consequences of what I've explained above: first, with a high wire resistance, your voltage will drop and you might not get the voltage you need. Second, having a thin wire with lots of amps will potentially melt the isolation and be a hazard.

So let's say we would accept any voltage loss and just don't want a hazardous situation. We take a wire of 1m. Then we run a certain amount of current though it which will produce heat in the wire. Now we double the wire length to 2m, so double the resistance. We run the same current through it which will produce double the amount of heat, but over double the amount of length. Unless you're coiling your wire I don't see how it should make for a more hazardous situation.

And the other way around, according to this calculator http://www.solar-wind.co.uk/cable-sizing-DC-cables.html if you have a 1cm wire and running 100 amps @ 12 volt you can do with 0.5 mm2. How is that possible?

Best Answer

The wire gauge you need is a function of several things.

  • The acceptable voltage drop or power loss (that appears to be the only thing considered in the website you linked). The voltage drop (and power loss) is proportional to wire length and inversely proportional to the cross-sectional area of the wire- in other words inversely proportional to the square of the wire diameter (assuming constant current).
  • The acceptable temperature rise. This is a function of the number of current-carrying wires bundled together, the environment (maximum ambient temperature and air pressure or altitude, for example), the insulation type, the wire type (some types of wire are plated to withstand higher temperatures than bare copper without corroding).
  • Regulatory requirements and other considerations- for example, the wire may be rated for 200°C insulation, but you might not want the wire to run that hot.
  • Fusing- the fuse or circuit breaker should protect the wire in the case of faults such as overload or short circuit.

Very short lengths of wire can depend on heat sinking through the ends (indeed, in a vacuum, that may be the main heat loss mechanism), but usually that's not taken into account.

Normally you'd run through a checklist such as the above to make sure ALL the requirements are satisfied simultaneously, so you might find that using PTFE insulated wire allows you to use AWG 18 wire, but because of the voltage drop limitation you'll have to use AWG 12 wire.