Continuing from the previous post above. Firstly I know how to calculate current in a DC situation.

However, since I am using an inverter that produces 220V at its output I would like some assistance in calculating the current consumption of a 30W LED and NOT a 50W LED. The specs given from the box for the 30W LED is 30W LED website:

  1. Supply voltage: 200-240AC

  2. Power: 30W

  3. CRI: RA>70.PF>0.9

Is it possible to determine the current consumption of the 30W LED from the specs given above?

Is the current consumption of 151mA correct, assuming a supply voltage of 220V AC? Using the following site of rapid tables

If it is correct then using a 18A-h is an overkill and since I will be running the light for only 2 hours(duration of the black out) a 3.5A-h will therefore suffice. Is this assumption correct?

The smallest SLA battery is 3.5A-h battery in my region.

Best Answer

You need to calculate using energy. For this problem Wh (watt-hour) is the most convenient.

Batteries are normally rated in A-h (Amp-Hour), not A/h (amps/hour) as you have specified

Output Energy = 30W * 2 hours = 60 Wh

Input energy = 3.5 A-h * 12 V = 42 Wh

So, you need more than a 3.5 A-h battery. And this doesn't even account for inefficiencies or the fact that many batteries shouldn't be discharged all the way if you want a long life.