Electrical – Diazed fuse heat dissipation

fusesheat

To be more precise, I'm interested in the amount of "created" heat during normal operation from a diazed 16 ampere fuse.

How hot will the fuse be after delivered 16A in seven hours with the voltage of 230VAC, in a nominal environment of 30C.

Best Answer

To solve that you need to calculate the power dissipated in the fuse (P = IR) and then the total thermal resistance between the fuse and the ambient. This would be then similar to a heatsink calculation and there are many examples of this on the web.

You are unlikely to find thermal resistance of a fuseholder published so your best bet would be to form an experiment:

  • Set up a fusebox and place the fuse in question into the holder.

  • Run an appropriate current through the fuse into a test load. This can be a low voltage setup such as car battery and lamps. Using low voltage would allow you to install a temperature sensor beside the fuse.

  • Run the test until the temperature stabilises.

  • Calculate the thermal resistance using formula:

    $$ R_{Th} = \frac {\Delta T}{P} $$

where \$R_{Th}\$ is the thermal resistance of your fuse and holder, \$ \Delta T \$ is the difference in temperature between your fuse and ambient and P is the power dissipated in the fuse. The result will be in K/W (kelvin per watt).

You can then use this figure to predict temperature rise for any other current through that fuse.