Electrical – Expected breaker temperature on a 208V 30A circuit with continuous 80% load

circuit breakercurrentpowertemperature

I have several cabinets of servers in a datacenter and each of these cabinets is on a dedicated 208V 30A circuit. The load on each of these circuits is 24A and one circuit is slightly higher (~24.6A).

Recently, a datacenter technician (not an electrician) got in touch with me and said that my breakers in the panel were hot and that I should reduce the load on the circuits.

He took measurements using an infrared gun on three circuits. He said that the temperature was 117F for two of them and 110F for the other. He said that the maximum temp should be 104F. The ambient temperature in the room is roughly 72F.

A couple questions:

  • Is it normal that my breaker temps are reaching 117F on a circuit that's at 80% load or slightly higher?

  • Is the max temp for a breaker really only 104F? If humans and sensitive electronics can handle 104F, then surely a breaker could handle much higher temperatures…

I understand that it's impossible to give an exact answer to these questions when I'm unable to provide specifics on the breaker panel — I'm just trying to get a general idea of what's 'reasonable' before I start pushing back on this request.

Best Answer

The breakers are likely rated for 40C (104F) ambient.That would be the meaning of 40C marked on the breaker. They are likely rated for connection to wire that has a 60/75C insulation temperature rating. That would also be marked on the breaker. The surface temperature of the breaker can be expected to be higher than the ambient temperature. A surface temperature of 47C should not be a problem if the ambient temperature is 40C, but 47C surface temperature in a 20C ambient could be a problem. That would mean the surface temperature has a 27C rise and would reach 67C in a 40C ambient. However the following information seems to indicate that the breaker is allowed to get hotter than the wire.

UL Surface Temperature Rise Limits

Non-metallic 60 deg. C

Metallic 35 deg. C

UL Terminal Temperature Rise

80% Rated CB 50 deg. C

100% Rated CB 60 deg. C

The above information was found in another forum, not directly from UL.

Related Topic