Electrical – why we say that in three phase system total power delivered to the balanced three-phase circuit is the same at any instant

powerthree phase

My question is: why we say that in three phase system total power delivered to the balanced three-phase circuit is the same at any instant?. This is how I understood that one phase at one point of time gives all the power then the second and third and so again from the beginning I do not know if my assumption is correct and I would like to hear your opinion.

thanks.

Best Answer

It comes down to the fact that in an ideal system, each phase has a sine waveform, and the well known relationship

$$sin(x)^2 + cos(x)^2 = 1 $$ for all X, and power is proportional to V^2.

Now that relationship obviously applies to 2 phases 90 degrees apart. How can you apply it to 3 phases 120 degrees apart?

Take the first phase as Sin(X). The other two are $$sin(x + 120 degrees)$$ and $$sin(x - 120 degrees)$$

A bit of vector analysis (draw the three out to illustrate) lets you resolve each of the latter two phases into sine and cosine components. So $$sin(x + 120) = A * sin(x) + B * cos(x)$$ I'll let you figure out the values of A and B.

Repeat for the other phase $$sin(x + 120) = C * sin(x) + D * cos(x)$$

Now square each of the three phases and sum over the squares... this is a bit of an exercise, but you should get

$$sin(x)^2 + cos(x)^2$$

which is of course 1.