Electronic – 3-phase 380 V to 3-phase 230 V

three phase

I have a portable bearing heater which works with 3-phase 230 V power supply.

My power supply is 3-phase 380 V. Is there any way to convert the 3-phase 380 V to 3-phase 230 V? Please note that since the equipment is portable, it is important that the solution be portable too.

I added the picture of wiring diagram of the equipment.
The manual indicates: The equipment is designed for 3 phase 230V power supply (Between each hot wire, 220 volts can be measured) when 2 phases are connected. it means 2 phases out of 3 phases are connected.

The supply power is 3-phase 380V,which means between each hot wire, 380 volts can be measured and between the neutral and any of hot wires, 220 volts can be measured
Wiring Diagram

Best Answer

enter image description here

Figure 1. Coloured up version for single-phase 230 V + N wiring.

It appears from the wiring diagram that you can just connect L3 to neutral instead with no internal modification.

The only concern should be that the components' insulation now has to withstand 230 V instead of \$ \frac {230}{\sqrt 3} \ \text V\$. You should check, if possible, that they are rated for that.