In my workshop I have a device that requires 220V 3 phase power, with a requirement of up to 1.5kVA. In North America, my wall outlet provides ~120V/15A single phases.

(EDIT – my device can take +/- 10% voltage, so anywhere from 220V to 240V 3 phase is fine.)

Doing some research, I found devices like these, called 'Variable Frequency Drives' that seem to take this type of single phase input and give the 3 phase output desired:

https://www.mcmaster.com/variable-frequency-drives

I am a noob at electronics, and I just want to confirm if I could buy one of these VFDs to solve my problem as described. I guess I would get the 2 HP version to match approximately 1.5kVA.

Thank you for any help, and open to other suggestions if this won't work.

Best Answer

There are VFDs that will accept 115V single phase input and give you a 230V 3 phase output. They use what is called a "voltage doubler" front-end rectifier, meaning they rectify the 115VAC to approx. 165VDC, then put it through a circuit that doubles the DC to 330VDC, then the inverter section uses PWM to recreates an output that MOTORS react to as if it is 230VAC 3 phase. The key point however is MOTORS; this can ONLY be used for 3 phase AC induction motors, you cannot use the output as a general 3 phase power supply source. it is the inductive nature of the motor that allows the PWM to become a pseudo-sine wave. Without the motor, it's just pulsating DC that changes direction.

Then there is the size issue. On a 15A 115V circuit, you can actually only load it to 80% of that continuously, so 12A. The largest 115V input VFD is for a 1-1/2HP motor, but the INPUT CURRENT on the 115VAC side is actually 20A; too much for a standard 15A circuit and actually, too much for even a 20A circuit (80% rule means a 20A circuit is only good for 16A continuous). For that reason, MOST of the companies that sell a 115V input VFD limit it to 1HP, and even those require a 20A circuit (the NEC allows you to use a 20A breaker for a 15A outlet if you use 12ga wire).