Electronic – Charging lead-acid batteries

batteriescharginglead-acid

Are there any special requirements for charging lead-acid batteries?

Best Answer

Charging lead-acid batteries with a power supply

Lead-acid batteries can be charged manually with a commercial power supply featuring voltage regulation and current limiting. Calculate the charge voltage according to the number of cells and desired voltage limit. Charging a 12-volt battery (6 cells) at a cell voltage limit of 2.40V, for example, would require a voltage setting of 14.40V.

The charge current for small lead-acid batteries should be set between 10% and 30% of the rated capacity (30% of a 2Ah battery would be 600mA). Larger batteries, such as those used in the automotive industry, are generally charged at lower current ratings. Cells constructed of a non-antimonial lead grid material allow higher charge currents but have a lower capacity. The cylindrical Cyclone is sealed and can sustain a pressure of up to 3.5 Bar (50 psi). A pressurized cell assists in the recombination of gases.

Observe the battery temperature, voltage and current during charge. Charge only at ambient temperatures and in a ventilated room. Once the battery is fully charged and the current has dropped to 3% of the rated current, the charge is completed. A good car battery will drop to about 40mA when fully charged; a bad battery may not fall below 100mA.

After full charge, remove the battery from the charger. If float charge is needed for operational readiness, lower the charge voltage to about 13.50V (2.25V/cell). Most chargers perform this function automatically. The float charge can be applied for an unlimited time.

--Information found here Hope This Helps!