Varistor Buffer Room – How Much is Required?

over-voltage-protectionvaristor

I am working on a circuit board design that uses a fuse resistor for protecting from short circuits and a varistor to protect from over voltage. The board is a simple power supply of only a few watts.

If I have a 275V varistor, what should I be looking for as the maximum voltage handling of the components protected by the varistor? I am not looking to use components with less than 275V handling, but want to know if I would need a 300V , 325V, etc. capable part behind the MOV for example. I have not been able to get a good feeling for the allowances that are required.

Thanks,

Jason

Best Answer

Idealy they should withstand surges up to the clamping voltage (where the varistor redirects all the current to ground). But for a 275VAC varistor (suitable for 220-250VAC), the clamping voltage is quiet high (600 to 750V) and you may not find all parts at or above these voltages, at least not at a reasonable price.

However varistors do reduce voltage under the clamping voltage, but at higher voltage than the rated voltage. A 275VAC varistor will reduce volatge from 300 or 350VAC but there is no precise limit and no precise resulting voltage which will be always higher. It's gradual up to the clamping voltage. So it's safe to have components rated 400 to 600VAC thought of course the higher the better.