Electronic – How to charge an AGM battery fast

battery-chargingcell-batteryinverterups

I have a 12V, 200AH AGM battery. The maximum charging current recommended by the manufacturer is 50 amps. Now, I need to connect two AGM 12v batteries in series to connect to the input of my 24 volt inverter with battery charger.

Is it possible to charge these AGM batteries in 5-6 hours?

What is the current and voltage required from battery charger in the inverter to charge the AGM batteries in 5 hours?

Is it safe to charge the battery in 5-6 hours? If not, what is the recommended charging time?

Any special precautions to be taken with this kind of battery charger?

Manufacturer battery specs

Best Answer

If you connect two batteries in series for charging, they MUST have the same state of charge - ideally, they would have been used in series, as a 24 volt battery. They should also be same make, model, and vintage/use history.

How long it will take to charge the batteries will depend on their state of charge. In theory, if they were fully discharged, and the charger could maintain a 50 amp charge current until they were fully charged, they would be fully charged in a little over four hours.

A smart charger will deliver its maximum current until the battery voltage under charge reaches about 28.8 volts (or so)(for a 24 volt battery), and will then reduce the current, maintaining 28.8 volts, then reduce the voltage to a float charge level.

See Batttery University for more details. (AGM batteries are a variation of lead-acid, which that page discusses.)