Help on MPPT for solar panels

bucksolar cellswitch-mode-power-supply

I am studying maximum power point tracking (MPPT), and I have found many setups using buck converter. Since buck converters step down the voltage, how can you have the maximum power at load if you step down the voltage? Do you increase the current so you get maximum power?

I am also confused about what load to use in the output of the buck converter. For example if you step down from a 17V solar panel input to a 5V output, and the maximum power from the solar panel is 10W, you need 2A current at the output (5V*2A = 10W), so your load should always be 2.5 \$\Omega\$? So if one changes the load, then the maximum power cannot be reached?

I hope someone can point me in the right direction, and correct me if my understanding is wrong.

Best Answer

First question : yes, a buck converter will increase the current delivered to the load as it reduces the voltage. (minus a small percentage loss)

Second question : if the output must be a constant 5V, and you always want to get the maximum power available from the panel, you must continually vary the load impedance to match the power available. So your load should ONLY be 2.5 ohms when the cell is actually delivering 10W. When a little haze reduces the cell's power to 5W (1 amp) the load must be 5 ohms, and so on. Otherwise the voltage delivered will vary from the desired 5V.

Most MPPT systems vary the load impedance by varying the charging current to a battery (or into a grid-tie inverter) If you don't have some sort of variable load (storage system, variable speed fan or even a heater!) you can't really implement MPPT.