Uninterruptible Power Supply – Battery Duration Calculation

batteriespowertransformerups

I am going to buy an UPS, and on website that sells is written that model contains battery with capacity 9 Ampere-hours, 12V DC output voltage and UPS resulting output voltage is 220 AC.

On the page it is written, that with 100 Watt consumer connected, UPS, working from battery will last for about 24 minutes. I do not understand why.

Power equation is

$$P = V • I$$

So, if power is 100 Watt and voltage is 220, then current is 100/220 = 0.4A. Hence, if capacity is 9Ah, it should last for 9/0.4 = 22 hours.

Even if by voltage, the battery voltage should be taken, and we have 100W/12V = 8.3A, then, still it should work more then 1 hour.

What am I missing? Additional power loss on voltage transforming from 12 to 220?

Best Answer

A battery may be stated as having a capacity of 9 Ah but many circuits won't be able to use all that capacity and, in your particular case that is self-evident. If the load is 100 watts and, it can be powered or sustained for 24 minutes then you need to refer that back to the 12 volt supply.

You do this by estimating the DC to AC conversion efficiency. This is usually no better than 80% hence, for a 100 watt AC load, your battery may be subject to a 125 watt DC load. The current will be 125 watts ÷ 12 volts which equals 10.42 amps.

If the battery and the circuit working together can only sustain load this for 24 minutes, that's a usable battery Ah rating of 4.2 Ah.

If the DC to AC power conversion efficiency is only 70% then your 12 volt battery may be seeing a DC load equivalent to 143 watts. That's a current of nearly 12 amps hence, for 24 minutes, that's a usable Ah rating of 4.76 Ah. Take your pick.

It's a little more complex than this if you dig into the details of course.