Voltage Drop Between Battery and Load

voltage

Why is the total length of wire in a circuit used to find the voltage drop between a battery and a load? Suppose the load is a distance l away from the battery. Wouldn't the voltage drop between the battery and the load be due to a length l of wire and not 2l? I understand that the current flows through a total distance of 2l of wire, but if the load is only a distance l away, why would it "see" a voltage drop due to 2l of wire? Is it possible to explain this with ohm's law and a simple circuit diagram?

Best Answer

Let's say we have a 12 volt source and a 12 ohm load located 100 feet away from each other.

Let's further state that the wire connecting them has a resistance of 100 milliohms per foot and - since each of the wires is 100 feet long - each of the wires will have a resistance of 1 ohm.

That's a total of 2 ohms, and being in series with the load's resistance of 12 ohms, that's a total 14 ohms.

Then, from Ohm's law we have:

$$ I = \frac{E}{R} = \frac{12V}{14\Omega} = 0.857\ amperes $$

and, since: $$ E = I R$$

the voltage drop in \$ \boldsymbol{each}\$ wire will be:

$$ E = I R = 0.857A \times 1 \Omega = 0.857 volt $$

Then, since there are two wires, each 100 feet long, connecting the supply to the load, the total drop in the wires will be twice that, or about 1.7 volts.