Electrical – Voltage loss over wire

currentvoltagewire

I need to run 12v across 30 feet of 18 guage wire. The device on the other end consumes 2 amps.

I have a 12v power supply (rated 3A) and I want to ensure the device on the other end gets the full 12v.

I found this post voltage loss calculation but I'm not clear on something. If my power supply can put out 3A and the device only needs 2A, does that mean there will be no voltage loss? (there is no sense wire) Will the full 12v arrive but there will be current loss?

I'm missing something basic here…


UPDATE:

I found 18 guage copper wire has resistance of 6.385 Ohm/1000 feet. so 6.385 * 60feet/1000feet * 2 amps = .76v loss.

From the comments it's apparent that voltage loss is unavoidable. So if I need 12v at the other end of the wire, I will need a power supply with 12.76v output (or adjustable). I already purchased a 12v switching power supply from ebay today for $8 – perhaps i bought too soon. Can these power supplies be adjusted (crack open the case)? Do 12v power supplies really put out exactly 12v? (Or do they put out 13v assume loss on wire, etc)

Best Answer

If my power supply can put out 3A and the device only needs 2A, does that mean there will be no voltage loss? (there is no sense wire)

I'm afraid not but the loss that does occur at 2 A will be less than that for 3 A.

Will the full 12v arrive but there will be current loss?

Current loss implies a partial short-circuit between the feed and return wire - e.g., poor or leaky insulation - and this is unlikely with modern insulating materials. As explained above the voltage will drop.


If you have an option, you could transmit the power at a higher voltage and reduced current and step down to 12 V at the load. AC won out over DC due to the ease of voltage transformation to minimise transmission line losses.


I don't know the exact current draw of the device yet, but I'm told 1 - 2 A is most likely. Its a computing device so it might be sensitive to the full 12v.

It is close to 100% certain that the computing device will use either 5 V or 3.3 V internally for the logic. The 12 V supply will be regulated down to the required voltage. There may be some other components such as display or backlight but these are most likely to be tolerant of a volt variation in voltage. i.e., The device requires 12 V nominal.

If there is no adjustment pot accessible from outside there won't be inside a sealed unit.